8/8/2017 8:28 AM | |
Joined: 10/11/2006 Last visit: 9/8/2025 Posts: 6039 Rating:
|
Hello, please note, that with p640 you set the current limitation (limitation of the setpoint) of the drive and not the overcurrent threshold. An overcurrent would only occur if the drive is not able to limit the current to the set value, e.g. caused by a too fast load change or any other fault like a short circuit - its a protection for the drive with an internal threshold which is higher than the rated maximum current of the device. The same occurs for the torque limitation, the drive maintains the torque setpoint always below or equal to the set maximum values, so for protecting the mechanical system you should setup the current and torque limits correctly. If you want to create a fault when the limit is exceeded, you can use the load monitoring function (see function diagram 8013 in list manual). |
With best regards, |
|
8/8/2017 12:41 PM | |
Joined: 6/28/2017 Last visit: 12/20/2022 Posts: 661 Rating:
|
Monitoring the load torque, briefly on screenshot. |