Hi smnsalinas, since the SINAMICS G120X is not available in SINAMICS Startdrive you won't be able to access the device using TIA Portal Openness. The easiest way to save the parameters would be by using the STARTER commissioning tool. An alternative solution would be reading the parameters using asynchronous communication like done in the application example 'SIMATIC S7-1200/S7-1500 and SIMOTION: Acyclic Data Exchange'. Kind regards |