Dear all i red this example in M420 catalog :
and I doubt the parameter P0759 should be 10v not 8v please send me a reply which clarifies this issue Thank you. AttachmentPages from 420_PLi_24525275_en_1006[1].pdf (182 Downloads) |
|
3/18/2011 11:20 AM | |
Posts: 739 Rating:
|
Hello, the 10V (4000h) = ASPmax and not P0759. ASPmax represents the highest analog setpoint (ASP= analog setpoint) P0759 can be adjusted as needed; see P0761. FAQ: http://support.automation.siemens.com/WW/view/en/38504226 |