8/8/2011 3:10 AM | |
Posts: 6 Rating:
|
Any body, help me please |
8/8/2011 9:52 AM | |
Posts: 6 Rating:
|
all expert, help me please....... |
8/8/2011 1:50 PM | |
Posts: 44 Rating:
|
Check operating status (operating manual chapter 6), check ON signal, check main contactor, check DC fuse, check speed feedback (P02), check reading parameter for setpoint ( P01), check reading parameter for current setpoint (P03) Have a look to the block diagram in chapter 4 of operating manual for better understanding, what´s going on. Link to the operating manual: http://support.automation.siemens.com/WW/view/en/21852470 regards frimos |
8/10/2011 8:18 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, Have you checked the 7 segement display? What is displays? Please see the attached file & analyise. Or put the display code along with wiring diagram so as to help you. Regards, DEEP. Attachment6RA22 operating display status manual.pdf (430 Downloads) |
8/12/2011 9:06 AM | |||||||||||||
Posts: 44 Rating:
|
I´m sorry, I don´t have the Z1004 manual available. since 6RA22 and Z1004 are phased out products it may be difficult to get it, maybe from the community? phase out was announced in 1994: The schedule to phase-out the product range is as follows:
To your problem: Did you try a new automatic current regulator optimization? Is everything correct with burden resistors? In the operating manual you find a list with the burden resistors. check also soldering of burden resistors (locatet on the power interface board). In the WWW I found this: http://www.meyle.de/vertragspartner/zubehoer-simoreg-k.php regards frimos |
||||||||||||
Last edited by: frimos at: 8/12/2011 9:07 AM |
|||||||||||||
8/17/2011 11:36 PM | |
Posts: 6 Rating:
|
Hallo Mr DEEP i have checked incoming voltage, and its balance on 403 vac Thanks
|