Hello, r0036 - It is calculated I2t value i.e. overload value in %. p0294 = 95% means when power module current reaches to alarm threshold value, ALARM 07805 will be triggered for power module overload & not over temp. When power module current reaches to 100% fault F30005 POWER UNIT OVERLOAD I2t will be triggered. r0037 - will display PM temp in deg centigrade. Its ALARM threshold is set in p0292 & corresponding alarm will be triggered whereas PM overtemp FAULT fault will be triggered when set PM temp is detected by sensor. Please refer attached sheet for more details. Hope this helps. AttachmentPM thermal detection.pdf (516 Downloads) |