Hello Vic; I can't help you with your last question, as I have not worked with the LP_Sched function Hopwever, I would like to clear up an issue that is frequent with newbies on the Siemens PID parameters: "Cycle" and the scan time of the function block. Whenever you use a PID block, in order for the calculations to be reliable, you must make sure that the parameter"Cycle"is the same (or at least a multiple of) the scantime of the block calling the PID. Or, as explained in the following FAQ: What should you watch out for when calling and assigning parameters to the controller functions in function blocks (S)FB41, (S)FB42 and (S)FB43? The "CYCLE" parameter corresponds to the scan time. The time between block calls must be configured here (e.g. time base of the OB35). |