10/20/2014 12:57 PM | |
Joined: 4/14/2010 Last visit: 6/26/2025 Posts: 525 Rating:
|
Dear Pegaia, With using TIA portal v12 i am able to control the PID loop for SSR heater circuit with pretuning, Fine tuning and PID manual input parameters option see attached. and using transister type output because relay type output having insufficient mechanical operation cycle for PWM. Proportional gain: 19.71297 Integral action Time: 63.45063 Derivative action Time: 16.00119 Derivative delay coefficient: 0.1 Proportional action weighting: 0.2638876 Derivative action weighting: 0.0 Sampling Time of PID algorithm: 1.500044 Controller structure: PID Thanks. AttachmentS7-1200 training.zip (665 Downloads) |
MS |
|
This contribution was helpful to
1 thankful Users |
3/24/2016 12:03 PM | |
Joined: 4/14/2010 Last visit: 6/26/2025 Posts: 525 Rating:
|
Dear Sarfraz i
want to control the heater through contactor please share me the sample
examples i am using k type thermocouple with s7 1200 thermocouple
module Please find Attached some snaps Regard's
AttachmentDesktop.zip (443 Downloads) |
MS |
|
Follow us on