3/10/2022 2:53 PM | |
Joined: 3/11/2019 Last visit: 9/1/2025 Posts: 1653 Rating:
|
Hi Izabella, you have configured a ET200SP CPU (1512SP) but in PLCSIM a regular CPU-1500 ist set. Please change the PLCSIM instance to a ET200SP (screenshot attached). SIMATIC S7-1500 S7-PLCSIM Advanced V3.0- Supported CPUsMaybe this helps. regards sancruz |
Last edited by: sancruz at: 03/10/2022 14:56:48Feedback appreciated, please rate |
|
3/10/2022 3:30 PM | |
Joined: 9/23/2019 Last visit: 12/5/2023 Posts: 3 Rating:
|
That worked, thank you both. Can you tell me why do I have to simulate an ET200SP when I'm working on a CPU 1512? |
3/12/2022 8:23 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
because 1512 is ET200SP Based PLC and not a s7-1500 PLC |
6/5/2023 2:08 PM | |
Posts: 1 Rating:
|
Hi, I tried changing to ET 200SP still recieving the same error. is there any other way to get it sorted? any solution would be highly appreciated. Thanks |