8/20/2020 3:09 PM | |
Joined: 10/5/2014 Last visit: 9/11/2025 Posts: 6 Rating:
|
Does anyone have solution to this problem? We have same request from customer, we need to have redundant profibus communication over DP coupler. Our system is S7-400H redundant, so more or less, its the same problem. How to communicate with two redundant systems over DP coupler. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/21/2020 08:04:31New subject after splitting |
|
8/20/2020 4:56 PM | |
Joined: 9/27/2006 Last visit: 9/13/2025 Posts: 12408 Rating:
|
Hello ctpdumag; I would suggest that each DP/DP coupler be configured separately, especially if you intend to reserve separate memory areas in your DCS for the data coming from each of the redundant CPUs in the S7-400H. I suggest you look at the DP/DP coupler manual (to learn how the coupler is configured between 2 S7 CPUs, and adapt the installation to connect to your own DCS. I ahve linked a discussion from an ABB forum showing a solution to use a DP/DP coupler between a S7 and a ABB DCS, which could serve as a guide for your project. SIMATIC DP/DP Coupler manual https://support.industry.siemens.com/cs/ww/en/view/1179382 How to configure Siemens DP/DP coupler in Compact control builder? (ABB) Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 08/20/2020 16:56:56 |
|
Follow us on