Hello Choppy apart from the DIP switch based setting of a Profibus address, software based node address assignment is generally done viaa Class 2 Master function called "SSA" (Set Slave Address). An S7 PLC is always a Class 1 Master and can NOT carry out this "SSA" command and you'll find more info on this subject at the Profibus SSA(set slave address) function thread. Having said the above (and just when you thought it can't be a "problem" in the S7), ABB's RPBA01 DP Slave interface also supports Node address setting via Parameter 918 (see itsmanualfor more on this). As such, your S7 could eitheruse the PKW mechanism to change this Parameter (if a PPO with PKW's is used) oracyclic DPV1 related Parameter writes (via SFC58/59or SFB52/53). Note too that the Node addresschange only becomes active after a drive power off/on soyour S7 program couldhave (accidently?) changed this parameter long beforeit becomes noted. Question is:Is the S7 program writing to Parameter 918? I hope this helps |
Cheers |
|