7/10/2014 9:23 AM | |
Joined: 10/11/2006 Last visit: 8/29/2025 Posts: 6037 Rating:
|
Hello, if you change between start and delta connection, you have to change the motordata`s. In VECTOR Mode there is parameter p133, where you can choose the motor configuration. Further info`s see: http://support.automation.siemens.com/WW/view/en/25338130 |
Last edited by: TechTeam at: 7/10/2014 9:23 AMWith best regards, |
|
7/14/2014 11:07 AM | |
Joined: 10/11/2006 Last visit: 8/29/2025 Posts: 6037 Rating:
|
Hello, P133 is not available with S120. For Motordataset please see: 12.2.2 DDS: Drive Data Set http://support.automation.siemens.com/WW/view/en/68042590 |
With best regards, |
|