9/17/2024 6:51 PM | |
Joined: 9/16/2024 Last visit: 10/25/2024 Posts: 9 Rating: (1) |
Thank you for answering, It seems that we can only share one picture at the same time, so I attached a pdf with the software's real & declared configurations + the hardware configuration and comments. We are using Freelance as our software, and ABB AC800FR automats, mostly working with PROFIBUS DP nodes. AttachmentForum siemens 1709.pdf (375 Downloads) |
9/17/2024 7:55 PM | |
Joined: 9/21/2012 Last visit: 11/7/2024 Posts: 4193 Rating: (472) |
You have BusAddress 2 set to two different devices, that might be the problem source. |
9/19/2024 2:43 PM | |
Joined: 9/16/2024 Last visit: 10/25/2024 Posts: 9 Rating: (1) |
I guess that is what we are going to do, then. Thank you for your time |