Dear Sir, How many module ET200SP TM Count1x 24 support? As I know, S7-1200 support max 6 HSCs. How about S7-1500 and ET200SP CPU? Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/14/2022 11:55:03New subject after splitting |
|
12/15/2022 9:17 AM | |
Joined: 8/29/2019 Last visit: 7/15/2024 Posts: 7 Rating:
|
Dear Sir, How about S7-1500, like 1511-1 PN. ? Thanks |
12/15/2022 9:42 AM | |
Joined: 1/21/2013 Last visit: 8/4/2024 Posts: 3044 Rating:
|
Hi DUY BINH,
it is not a question of the PROFINET controller used. The limiting factor is the SIMATIC ET200SP system. At least as long as you use a counter module of the ET 200SP series. If you use a SIMATIC S7-1500, TM count 2x24V in the central setup of a S7-1500 (or also at a ET200MP), then the limitations look different. Kind regards |