5/8/2025 2:16 PM | |
Joined: 7/5/2013 Last visit: 9/10/2025 Posts: 3241 Rating:
|
Hi, generally Simatic Automation Tool might be an option for that task, but, I guess, you activated "Set IP address in the project" in the PLC properties. In SIMATIC Automation Tool user guide chapter 4.1 it says that "IP address is set directly at the device" must be activated. Regards, Frink |
Pi is exactly three! |
|
5/9/2025 3:42 PM | |
Joined: 10/18/2024 Last visit: 5/14/2025 Posts: 28 Rating:
|
Hi Frink, Thanks for the quick reply and useful info. I have managed to do it using TIA via a Tosibox. |