Hi, you can also delete the file "S7_JOB.SYS" and the folder "SIMATIC.S7S" from the SIMATIC Memory Card. Afterwards the SMC is "blank" and without the existing project including the password. Afterwards it is also possible to transfer the program via online connection. Change the password in hw config before, otherwhise you will run into the same issue again. The meaning of the files and how to transfer the program to SMC directly is also described here: How do you create the project data for the SMC so that you can download the project to the S7-1200/S7-1500 CPU even without STEP 7 (TIA Portal)?