Hi, I'm struggling with communication between TP1200 Comfort V17.0.0.0 update 8 not communicating with 1518f V3.1. I'm using TIA Portal V20 update 3.
I've tried to download newer image from page https://support.industry.siemens.com/cs/de/en/view/109825750, but newer images can be downloaded only some new software HMI PIU Installer. But newest ones are V17. App is very Siemens, when I try to download V17 images, app just throws an error with no error code/message. Did Siemens changes anything recently regarding HMI communication? |
Last edited by: Petr Broza at: 09/12/2025 04:14:10adding tia v Last edited by: Moderator_Lan at: 09/12/2025 06:03:49link optimized TIA V20 update 3 |
|
9/12/2025 4:27 AM | |
Joined: 5/27/2014 Last visit: 9/12/2025 Posts: 122 Rating:
|
Siemens now utilize SSL/TLS encryption for establishing a connection for HMIs V17.0. and higher. Long story short, since there are certificates in play, there need to be correct date & time set on HMI (possibly PLC?!?). See following KBs: No connection to PLC after WinCC Panel Images V17 Update 6 Questions and answers about the security features as of TIA Portal V17 |
Last edited by: Moderator_Lan at: 09/12/2025 06:04:24links optimized TIA V20 update 3 |
|