2/27/2016 9:19 AM | |
Posts: 2 Rating: (0) |
Hello, we have an problem with simodrive 611 error E:A039. our inverter code is 6sn1123-1ab00-0ca1. Can you advise us something how to overcome this ıssue? Also, Would you share us the error code list about that series? We will wait your interest,immediately. thanks&best regards Mr.Nurullah ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 2/29/2016 3:54:02 PMNew subject after splitting |
|
2/28/2016 7:45 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878) |
Hello, Error 039 means - Error during power section identification. If the alarm has displayed while machine is in running condition from quite long time, then control module might be faulty. Try by replacing it. If the alarm has displayed during commissioning or service job, please check P1106 for correct value of parameter. Refer attached sheet for detail fault description & follow this link chapter 7.0 for complete fault code list of 611 simodrives. |
This contribution was helpful to1 thankful Users |
3/15/2017 8:35 AM | |
Posts: 1 Rating: (0) |
I also have this error that has not processed yet. Please indicate your handling.Thank so much |
3/16/2017 2:35 PM | |
Posts: 2964 Rating: (484)
|
Hello, Normally this type of errors happen during any vibrations in the drive panel. You can remove the card and re plug it back in the LT module. Once the card is removed you can find in the LT module female flat connector placed where the control card pins are going to sit on this, ensure the cable is sitting are proper. Reconfigure/ Delete this particular axis through Simocom u and check. Regards, Prakash
|