3/5/2013 2:56 AM | |
Joined: 10/7/2005 Last visit: 9/14/2025 Posts: 3049 Rating:
|
Hello vipz
It depends, older 314C-2DP's did not support DPV1, any newer ones do in which case DPV1 is automatically available/enabled whether you use its feature or not. I suggest you punch in the part number of your CPU at https://support.automation.siemens.comand check its technical spec (see6ES7314-6CH04-0AB0as an example, DPV1 is listed as supported in the DP Master properties of the 2nd interface).
It will be whatever data record you want to read from or write to the SIMOCODE. Have a look at Appendix B of the System Manual SIMOCODE pro which details the numbers and structures of all available data records. Note that you could also use SFC58/59 in which case the data record number is passed on to the Parameter with the name "RECNUM". I hope this helps |
Cheers |
|
This contribution was helpful to
2 thankful Users |
3/5/2013 8:04 AM | |
Joined: 9/2/2012 Last visit: 7/10/2025 Posts: 712 Rating:
|
Dear frits, its working.. thanks VIPZ |
|
|
This contribution was helpful to
2 thankful Users |