4/9/2020 3:53 PM | |
Posts: 5 Rating: (0) |
but I can't see hardware interrupt opion there(attach) |
4/9/2020 3:53 PM | |
Joined: 9/27/2006 Last visit: 9/28/2024 Posts: 12283 Rating: (2685) |
Hello Automotiv3; Here is additional information on setting triggers for OB40 (Hardware interrupt): What is a hardware interrupt and how do they work in the S7-300 system? https://support.industry.siemens.com/cs/ww/en/view/23657941 The screenshot below is taken from the System and Standard Functions manual: https://support.industry.siemens.com/cs/ww/en/view/109751826 Edit: I just saw you last reply. To introduce an new OB in your program, you must create it (New Block, type: OB, then give it a name: 40). Then, in theblocks local data (that you can use in the OB40 programming, you can set the trigger signal to launch the OB. From the first link above: Alarm OBs in SIMATIC S7-300: Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 04/09/2020 15:59:37 |
|
4/9/2020 3:55 PM | |
Joined: 5/12/2006 Last visit: 9/30/2024 Posts: 22381 Rating: (3015)
|
Hi, you must go to the properties of the IO Slot /module of wago, not to the headmodule.
Christoph |
4/9/2020 4:00 PM | |
Posts: 5 Rating: (0) |
I still can't see hardware interrupt(attch) |
4/9/2020 4:33 PM | |
Joined: 2/5/2013 Last visit: 9/27/2024 Posts: 321 Rating: (74) |
Hi Automotiv3, May be this will help you.Please check attachment. Read manual for diagnostics Page no 96 Search it on Google.Link Br, AmolG. AttachmentThird_Party_IO.pdf (294 Downloads) |
Please rate it. |
|
This contribution was helpful to1 thankful Users |
Follow us on