Dear all, Currently, I am experiencing an issue with one AP Scalance W774-1 RJ45 and two Client Modules (CM) 734-1 RJ45. I have a RCoax Antenna that is 200 meters long, arranged in a circular loop. Both ends of the RCoax antenna are connected to two Rcoax Cables 6XV1875-5AH10, and these cables are connected to the two antenna ports on the AP. The configurations of the AP can be seen in the attached image. The problem I am encountering is that after a period of time, the CMs are unable to ping even though the AP is still functioning normally, and the connection to the two CMs can still be seen on the AP. I suspect that connecting both ends of the RCoax Antenna to the same AP may be causing this issue; however, using only one AP antenna for a 200m length seems too long. Is there any solution you could suggest for us? Currently, we are also unable to split the RCoax Antenna into two segments. Attachmentap-config.zip (283 Downloads) |
8/29/2024 11:48 AM | |
Joined: 4/25/2017 Last visit: 10/11/2024 Posts: 430 Rating: (66) |
Hi, First, connecting RCoax to both interfaces into both ends is a bad idea and will get you into troubles if not very experienced. You could use PowerSplitters. Please check the RCoax system manual for that: https://support.industry.siemens.com/cs/ww/en/view/109480869 Max Segments per AP i would suggest: One sided feedin: 90m Middle feed in with Power splitter: 2x80m |
Best Regards, |
|