Have you allowed Modbus access in the file properties? |
8/30/2024 4:14 PM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34207 Rating: (4261)
|
In attachment a screen video from a test with a real LOGO! 8.3 and a Modbus Master Simulation program.
AttachmentScreencast 2024-08-30 18-03-41.zip (226 Downloads) |
This contribution was helpful to1 thankful Users |
9/3/2024 1:16 PM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34207 Rating: (4261)
|
You should never use DHCP for PLCs. LOGO! wants a fixed IP address. |