11/21/2023 7:55 AM | |
Joined: 8/21/2023 Last visit: 10/21/2024 Posts: 4 Rating: (0) |
Hello! i have H system with 2 s7-400 CPU. we had a problem with the power supply on the (4)IM-153-2, we replaced it, after this we periodically have error “Lost of redundancy at DP Slave 4”. Red indicator SF on iM-153-2 and and error in diagnostic buffer of CPU. We replaced the module (4)IM-153-2, but this did not solve the problem; the error periodically appears on the module and controller. We checked cables and connectors. Tell me possible solutions AttachmentImages.zip (357 Downloads) |
Last edited by: Jen_Moderator at: 11/21/2023 11:12:38Text formatting optimized. Added files as .zip file. |
|
2/12/2024 11:20 AM | |
Joined: 8/21/2023 Last visit: 10/21/2024 Posts: 4 Rating: (0) |
Solution - replacing the bus between modules |
2/12/2024 4:16 PM | |
Joined: 6/7/2018 Last visit: 10/2/2024 Posts: 3 Rating: (0) |
Hi, I have the same problem. Can you please explain what you did in the end to fix this problem? |