9/17/2008 5:06 PM | |
Posts: 271 Rating:
|
Hello Elemon, Here is a link to the Simodrive 611 analog start up guide: www.automation.siemens.com/doconweb/pdf/SINUMERIK_SIMODRIVE_07_2008_E/IAA.pdf?p=1#page=1&view=FitBH,0&pagemode=none Go to page 133 of 399 where you will be in the HS (haupt spindle) section of the manual. There you'll find all the parameters and start up information. One section to pay particular attention to are the notes on page 139 regarding write protection, transfering data to the FEPROM, etc. Also, the motor data must be entered correctly in parameters P-159to P-178. It is important that the encoder resolution be correct in P-098 (default: 2048 PPR). Next is P-014 may limit the output speed. See section 3.1. Look at P-001 and compare to P-002 to see that the scaling of the spindle speed is correct. P-029 sets the maximum motor speed. P-096 is the motor code number. Make sure you have the correct motor type selected. See section 6.2 on page 229. Hope this helps... |
9/17/2008 5:55 PM | |
Posts: 4 Rating:
|
Thank You for the Link Dave! |
9/19/2008 2:04 PM | |
Posts: 4 Rating:
|
Hello Dave, |