Joined: 4/16/2014 Last visit: 7/29/2024 Posts: 20 Rating: (1) |
Accidentally put the sensor in Current sensor mode. The display shows the letter "C" Does not respond to buttons. How to get out of this mode? |
10/16/2019 10:33 AM | |
Joined: 4/16/2014 Last visit: 7/29/2024 Posts: 20 Rating: (1) |
7MF 4433-1DA02-1AB7-Z FW: 0011.03.06 HW: 02.07.01 Does not respond to buttons. C on display: [snip] Device status: [snip] Properties: [snip] Simulation windows: [snip] Analog output saturation indicator: [snip] How change device status to good? AttachmentImages.zip (437 Downloads) |
Last edited by: Jen_Moderator at: 11/30/2023 09:52:49Links removed and files attached as .zip file. |
|
11/30/2023 8:29 AM | |
Joined: 9/26/2020 Last visit: 12/12/2023 Posts: 2 Rating: (0) |
There was an error (hardware firmware alarm) plus letter "C" in mode on bottom left side of display on a SITRANS P DS III which appeared by itself before connecting to transmitter while transmitter was working for a long time. (attached pdf) after connecting via Endress+Hauser HART communicator (HW: Commubox - SW: Field Xpert SMT70) to transmitter by factory reset the error gone but letter "C" remained . in this situation all three buttons still were disabled. on Hart communicator software Field Xpert (attached pdf), found out that in section "Hart communication" there is an option "Current output active" which was inactive. only it needs to change it to Active.
AttachmentSITRANS-mode-C.pdf (532 Downloads) |