Hi Chris, I saw this article on the support site:Desigo PX controllers: No alarm notification to stationary alarm receivers using ... - ID: 109990747 - Industry Support Siemens This could be your problem if you have the latest FW version of the PXC controller. They recommend a downgrade in this article. ================================================================= RecommendationDue to the above facts, we recommend for the time being not to install from the XWP_Firmware-Library_V6.30.495 the FW_PX..._V6.00.345 or FW_PX..._V6.30.037 on any PX devices. Note: For Desigo PX sites where the specified affected firmware is already installed, we strongly recommend downgrading to the previous firmware:
======================================================================== Best regards, Fons |
Last edited by: Moderator_Lan at: 08/25/2025 13:41:28link optimized |
|
This contribution was helpful to
1 thankful Users |
8/26/2025 5:40 AM | |
Joined: 10/12/2023 Last visit: 9/1/2025 Posts: 116 Rating:
|
Hello Fons, We have X.338 FW on all PXCs, but thanks for the helpful article. |