4/23/2013 10:33 AM | |
Joined: 5/12/2006 Last visit: 9/15/2025 Posts: 22710 Rating:
|
Hello, which STARTER Version do you use? And which FW is stored on the CU240? I think you have the same problems which is described here: /tf/WW/en/Posts/88525#top Regards Christoph |
Last edited by: ChristophD at: 4/23/2013 10:37 AM |
|
4/23/2013 10:37 AM | |
Joined: 10/11/2006 Last visit: 9/15/2025 Posts: 6040 Rating:
|
Hello, If you can´t get any informations about the contacted Control Unit its possible that you have a CU240E-2 with version 4.5. In this case you need at least Starter 4.3.1 to get a running communication for commissioning the drive. The actual starter software - Version 4.3.2 - can be found here: http://support.automation.siemens.com/WW/view/en/26233208 |
With best regards, |
|
4/24/2013 4:12 AM | |
Posts: 50 Rating:
|
is CU240E I installed the starter v4.1 but i cant communicate with the CU |
Follow us on