Hello sir i have a sum problem to use of sm 1232 analog output module 6ES7 232-4HD32-0XB0 v2.0 i am give 24v dc only but all outputs are automatically on without any command ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 06/26/2024 13:47:49New subject after splitting |
|
6/26/2024 2:30 PM | |
Joined: 7/7/2010 Last visit: 11/18/2024 Posts: 15406 Rating: (2446)
|
As soon as the hardware configuration is loaded to the PLC, the analog outputs are operating as defined in that configuration. If the HW config states all are enabled, then they will indeed all turn "on". It is up to you to assign proper values to the analog output QW# tags is the proper range (-27648 to 27648, or 0-27648).
|