3/5/2015 3:11 PM | |
Joined: 11/17/2010 Last visit: 9/12/2024 Posts: 216 Rating: (40) |
Hi, I want to upgrade my new communication module CM 1241 (6ES7241-1AH32-0XB0) with firmware V2.1.0. CPU is in STOP mode. I tried to upgrade the module using TIA Portal V13 SP1 Upd 1 and the following message box is displayed : The module is not currently ready for firmware update. So, I tried using WebServer of CPU 1214 (6ES7214-1HG40-0XB0). When I select the firmware file, Status field display : "This firmware is suitable". But, when I click on Run update button, Status field display : "The selected firmware file is not suitable for this module".
I have downloaded the firmware from this link here. Thank you for your help. Regards. |
3/5/2015 4:00 PM | |
Joined: 7/7/2010 Last visit: 10/14/2024 Posts: 15302 Rating: (2427)
|
What firmware version is the CM-1241 right now? If it is 1.x.x, that means there was a hardware revision between what you have and the firmware you are attempting to install. I do not know if it is possible to upgrade firmware when the hardware changes. Sometimes it is possible, but not a guarantee. If you do not have a PLC that supports CM1241 firmware 2.1 (it might need a hardware support pack, though for V13 SP1, you would think everything is supported), it might not allow you to upgrade the firmware. More details about the plc you are using for the firmware update and the current firmware in the module.
|
science guy |
|
3/5/2015 4:46 PM | |
Joined: 11/17/2010 Last visit: 9/12/2024 Posts: 216 Rating: (40) |
Thanks for your quick reply. Firmware versions : CM1241 : V2.0.3. CPU : V4.1.1. (Upgraded this morning). |
7/14/2015 1:44 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
|
Follow us on