12/21/2008 12:20 PM | |
Joined: 9/27/2006 Last visit: 10/12/2024 Posts: 12287 Rating: (2685) |
Hello Abod; I f you look at the following attached document, you will see that theinterface modulepairIM 460-1 and IM 461-1 can only support one sender and one reciever, and that the maximum distance between the two is 1,5 m at the most. So it is designed for local (inside the panel) applications only; the supported module typesare also limited, as the K-bus is not supported on the dedicated interface. You can study this information (and much more)in chapter 6 of the following manual: http://support.automation.siemens.com/WW/view/en/1117740 Hope this helps, Daniel Chartier |
12/21/2008 1:09 PM | |
Posts: 2 Rating: (0) |
thanks Danial for your help....i understand now
marry christmas |
12/22/2008 1:54 PM | |
Joined: 4/24/2006 Last visit: 10/10/2024 Posts: 8745 Rating: (1168) |
Hi Daniel, I think it's possible to connect two Expansion Racks , the IM460-1 (sender) has two connectors. At each connector you can use IM461-1 (Receiver). See in mentioned manual Chapter 6; par. 6.3 (You can only connect one ER per line) The maximum distance between Sender and Receiver is 1,5 m. Best regards, Wizard |
Last edited by: Wizard at: 12/22/2008 1:59 PMLast edited by: Wizard at: 12/22/2008 1:55 PM |
|