12/7/2010 3:48 PM | |
Posts: 2348 Rating:
|
Please upload diag buffer - really hard to see something on that picture. |
12/8/2010 12:27 AM | |
Joined: 10/7/2005 Last visit: 9/10/2024 Posts: 3020 Rating:
|
I agree with Aretand can for now only add the error description for your Event ID 4xE7 (don't forget to use the"Help on Event" button in he Diagostic buffer): The standby CPU has aborted its link-up/update and switched to STOP mode or DEFECTIVE mode. (The exact cause of this is listed in the referenced event of the partner CPU.) The H system continues to run in solo mode. |
Cheers |
|
12/15/2010 7:34 AM | |
Posts: 37 Rating:
|
Aret said right, send me the CPU buffer and I will tell you what happened |
12/16/2010 9:43 AM | |
Posts: 947 Rating:
|
See (check)indicator on sync modules. all must light. may be 1 sync modul or optocable is fault |
Last edited by: gre_m at: 12/16/2010 5:51 PM |
|
12/22/2010 9:29 AM | |
Joined: 12/7/2010 Last visit: 7/25/2024 Posts: 3 Rating:
|
Sorry for the delay!
AttachmentDiagnose.pdf (203 Downloads) |