9/5/2013 12:03 PM | |
Posts: 22 Rating: (2) |
Try downloading the hardware and software alongwith system data in the eprom card of both the CPUs |
Last edited by: Nandlal Pal at: 9/5/2013 12:03 PM |
|
9/5/2013 5:44 PM | |
Posts: 3 Rating: (0) |
Hi Nandal, Thanks for your reply and what you have been suggested is not working, whereas we dont have EPROM here we are using RAM. Thanks mathakala
|
9/24/2013 2:47 PM | |
Joined: 4/3/2013 Last visit: 12/15/2023 Posts: 7 Rating: (0) |
Hello,
check please the Rack.Nr of Master and Standby PLC. Master must have Rack number 0 and the Standby PLC Rack number 1.you find a switch on the back of the PLC'sfor thisRack number adjustement. ckeck please the correct connection and setup of Sync-modulesand possibledefective modules (e.g. curved connection pins of Sync modules) Note: if you use the old Sync-Module, the closing cover must be permanently attached with th Sync-module in order to activate the micro switch of Synch modules. Please use also the Service Request from Online Support for more Details. http://support.automation.siemens.com/WW/view/en/16605032 |
Last edited by: BigCologne at: 9/25/2013 1:51 PM |
|