7/15/2024 7:59 PM | |
Joined: 6/28/2024 Last visit: 7/15/2024 Posts: 1 Rating: (0) |
Také mám stejný problém. Typy mám INT oba dva. Jak PV tak CV. U obou DOWN čítačů stejný problém. Místo aktuálního čísla ukazuje 512 nabo dokonce 256, dle toho kam se čítač směrem dolů dostane. I have the same problem. I have both INT types. Both PV and CV. Same problem with both DOWN counters. Instead of the actual number it shows 512 or even 256, depending on where the counter goes down ------------------------------------------------------------------------------------------ |
Last edited by: Wit_Moderator at: 07/16/2024 13:42:51New subject after splitting |
|
7/16/2024 7:15 PM | |
Joined: 7/7/2010 Last visit: 10/18/2024 Posts: 15327 Rating: (2432)
|
Please post screenshots of your problem down counters. Also, please show the PLC tag table sorted by address the tags used for the counter PV and CV. If you have any yellow highlighted tags, fix that problem and your counters may start working.
|
science guy |
|