Hi, D_ACT_DP can only be used to deactivate the whole io-device, but not submodules. As already mentioned, option handling (configuration control) is what you are looking for. There is also an FAQ: Configuring standard machines in TIA Portal (configuration control)What should you watch for with configuration control (option handling) with fail-safe controllers S7-1200 and S7-1500?regards sancruz |