9/30/2009 10:27 AM | |
Joined: 10/19/2005 Last visit: 11/30/2020 Posts: 1611 Rating:
|
Hi, |
Last edited by: The Brain at: 9/30/2009 10:28 AM |
|
10/9/2009 4:22 PM | |
Joined: 1/4/2007 Last visit: 7/11/2024 Posts: 1134 Rating:
|
Hello createstars, Attached you can find a screenshot of the DR4 into the file “DR4_Limit_Values.JPG”: Attachmentpictures.zip (197 Downloads) |
10/26/2009 3:19 PM | |
Joined: 1/4/2007 Last visit: 7/11/2024 Posts: 1134 Rating:
|
Hello createstars, The error message "weight outside zero definition range" means: The belt scale is out of the zeroing definition range. You can define the zeroing definition range into the DR3 / Calibration param. 3: “Zeroing val - (%)” and “Zeroing + (%)” The numeric value means the maximum positiv and negative weight for zeroing in % of the parameter “Maximum range 1” into the DR3 / Calibration param. 2. (See also the first page of the attached file.) For example: “Maximum range 1” = 200.0“ Zeroing val - (%)” = 1“ Zeroing + (%)” = 3 The zeroing definition range is here: -2.0 ... +6.0 kg (or tons or ...) of the gross weight. Also you have to undershoot the limit into the DR5 / Load: “Max. zeroing range load value (0,1%)” (See also the second page of the attached file.) If the two criteria above (maximum positiv / negative weight for zeroing AND Max. zeroing range load value) are conform, the status-bit “Dynamic zero range” is true. (See also the third page of the attached file.) If this status-bit is true, you can execute the command “zeroing”. Best regards Siwarexi AttachmentFTC_B.pdf (199 Downloads) |