7/1/2014 9:47 AM | |
Joined: 6/1/2010 Last visit: 7/9/2024 Posts: 160 Rating: (1) |
Dear experts, [As per attached file] In S7416-2DP plc hardware how both IM 460-0 to IM 461-0 connection doneto each other as interfacing between two racks. I would like to know how to connect them in other new configured project of same hardware. In field Hardware connection was completely done but how tomake itin 'simatic manager software application'. sorry for my english. Thank you for your attention. AttachmentC:\Documents and Settings\sms E&A\Desktop\IM MODULE in Hardware.zip (394 Downloads) |
Last edited by: A9K at: 7/1/2014 9:48 AMA9K |
|
7/1/2014 6:28 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308) |
HelloA9K, Please, check the attached picture. Best regards, H-H
|
This contribution was helpful to1 thankful Users |
7/3/2014 5:16 AM | |
Joined: 6/1/2010 Last visit: 7/9/2024 Posts: 160 Rating: (1) |
Thank you for your suggested steps to configure IM ...... it works. |
A9K |
|
This contribution was helpful to1 thankful Users |