2/12/2025 7:27 AM | |
Joined: 6/22/2009 Last visit: 6/6/2025 Posts: 63 Rating:
|
We are proposing a configuration (attached) with CPU 1215C as MRP Manager and ET200SP as MRP Clients in a Ring. The Field side cables are Fibre Optic. The switches are third-party (Phoenix Contact) managed switches with 4 RJ45+ 2 SFP ports. At the CPU location we are tapping from the same switch for SCADA and HMI. Is the configuration correct?
AttachmentConfig.pdf (250 Downloads) |
2/13/2025 12:03 AM | |
Joined: 10/7/2005 Last visit: 9/14/2025 Posts: 3049 Rating:
|
Hi DolaMam a couple of things to change and check in your Topology: 1.) CPU and each ET200SP will only have a single Ethernet patch lead connection to their switch (not two as shown in your sketch) 2.) The Phoenix Contact Switches will need to support MRP (and most likely do, but please check) and be the MRP Clients in the FO ring |
Cheers |
|
This contribution was helpful to