hi, can you help me this,on what basis redundancy work,on what condition switch over take place ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/28/2019 07:19:33New subject after splitting |
|
10/29/2019 8:01 AM | |
Posts: 5 Rating: (0) |
for s7 417-5h redundancy controller |
10/29/2019 2:53 PM | |
Joined: 9/27/2006 Last visit: 11/16/2024 Posts: 12294 Rating: (2691)
|
Hello sussac; Here would be the quick and simple reply: any fault detected on a CPU in a H-system, on the remote I/O channels or in the fiber-optic cables dedicated to redundancy on a S7-400H will provoque an immediate switchover (change of active primary CPU to the stand-by). This is explained in the following manual, which you should study and keep near you when wiorking with a S7-400H system: SIMATIC Fault-tolerant systems S7-400H (V6.0) https://support.industry.siemens.com/cs/us/en/view/82478488 The extracted screeshot below comes from that manual. Other automation sites discuss Siemens issues, this article might be interesting: https://control.com/thread/1026176237#1026176237 Hope this helps, Daniel Chartier |