6/2/2014 12:10 PM | |
Joined: 4/19/2008 Last visit: 9/3/2024 Posts: 1525 Rating: (159) |
Hello RIAN Che, You can Conenct the Hard Device to the Normal Analog Input Module (6ES7-7KF02-0AB0) For the Parameter the Hard Device you have to Used Hard Progaming Device, That you have to connect to the Terminal of the Panel or the Direct to the Instrument, HART – Learning More about HART If you want to used the HART Configuration should be done from Your ES then you need the PDM with 6ES7331-7TF01-0AB0SM331, 8AI, 0/4-20MA HART |
Ammy |
|
This contribution was helpful to5 thankful Users |
6/2/2014 1:20 PM | |
Joined: 4/21/2006 Last visit: 8/27/2024 Posts: 510 Rating: (24) |
New question was splitted to a new thread: HART signals => different HART cards? |
6/3/2014 11:48 AM | |
Joined: 8/27/2010 Last visit: 4/13/2024 Posts: 417 Rating: (37) |
Please look atthis manual, page 378 And make a search for "intergation time" for detailed description: STEP 7 parameter for analog input modules. The integration time is equivalent to the inverse value of the → noise suppression frequency in ms. The measured value resolution is directly proportional to the selected integration time, that is, the measured value resolution increases in proportion to length of the integration time at the analog input channel. //2.5 ms; 16.6 ms; 20 ms; 100 ms corresponds to interference frequency suppression from 400 Hz; 60 Hz; 50 Hz; 10 Hz Please check this manualtoo. |
Last edited by: olloy at: 6/3/2014 11:59 AMBTW, default setting is 50 Hz that means 20 ms of intergation time. Leave it "as is" and connect your sensor finally) Last edited by: olloy at: 6/3/2014 11:54 AMlinks added Last edited by: olloy at: 6/3/2014 11:51 AM |
|
This contribution was helpful to2 thankful Users |
Follow us on