6/26/2011 7:46 AM | |
Joined: 6/20/2011 Last visit: 11/13/2024 Posts: 27 Rating: (0) |
hi all, i started a redundant project , my configration,, CPU 412-3H --> 2 piece, H sync submodule --> 4 piece, CP443-1 --> 2 piece, 6GK7 443-1EX20-0XE0 i using as i/o module IM153-2 (153-2BA02-0XB0) and S7-300 module , every thing this ok without CP443-1 ... when i reset both of CPU and add CP 443-1 when i turn on subsystems , both redundant go to fault ... both of CP 443-1 iluminate INTF and BUSF on and this fault make fault for CPU and could not RUN mode , after download of hardware to PLC continue this error too ... i want ethernet communicationfor WinCC scada and operator panels. i usingtwo CP443-1 for this project but i dont know why make fault i must deliver this project in weekend ... please Help my friends thanks Splitted from S7-400 Redundant system and CP 443-1 Configration. AttachmentRED2_2.zip (234 Downloads) |
Last edited by: O_Moderator at: 6/27/2011 1:55 PMnew subject after splitting Last edited by: fk19744 at: 6/26/2011 8:13 AM |
|
6/26/2011 4:12 PM | |
Posts: 947 Rating: (45) |
insert "check Mac adress/use Iso-protocol" (red ring in picture ) - need make in each CPH-system. May be should uncheck "use web-server" - green ring. I would not use IP (uncheck IP-protocol). see attach
Attachmenthh.ZIP (138 Downloads) |