2/8/2009 7:01 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (318)
|
Hi, The answers on your questions: 1. The number of bytes are the limitation, not the number of slaves, you could use 240 Byte in- and output; 2. An CPU could used as PROFIBUS slave behind the Y-Link, but there are no intelligent things possibe, like going online; 3. See 1. and 2.; Handbook Y-Link: Bus links DP-PA coupler DP-PA link and Y link |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|