3/29/2024 11:49 AM | |
Joined: 4/10/2020 Last visit: 11/4/2024 Posts: 77 Rating: (1) |
Anyone can give me some help please ? |
4/2/2024 3:06 PM | |
Joined: 10/11/2006 Last visit: 11/8/2024 Posts: 5935 Rating: (815)
|
Hello Nicolas, See also section 5.3.1 |
With best regards, |
|
This contribution was helpful to1 thankful Users |
11/8/2024 11:51 AM | |
Joined: 10/11/2006 Last visit: 11/8/2024 Posts: 5935 Rating: (815)
|
Dear AcaStrucnjak, this is an issue of Startdrive in function view. The selection is greyed if time delay time p9652 is "0". You can change p9652 to a value >0 to activate the field or you can switch to parameter view and change p9653=1 there. SS1 with external stop is also possible using safety integrated basic functions, see safety integrated function manual section 5.1.2.2 https://support.industry.siemens.com/cs/ww/en/view/109781535 |
Last edited by: Technology Team at: 11/08/2024 12:30:27With best regards, |
|