11/28/2017 4:18 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello hamed; Compare your list with the one attached below. This Control word description table was taken from the following manual: https://support.industry.siemens.com/cs/fr/en/view/6586565 In the attached table, note that bit 0 is at the top of the table, bit 15 is at the bottom. Bit 12, both in your screenshot and in the MM4 control word table, is marked "unused". You could simply modify your screen, replacing the "-------" line with "Unused", simply to remove any doubts or further questions. Hope this helps, |
Last edited by: Jen_Moderator at: 11/29/2017 11:16:18 AMInserted right link. |
|
This contribution was helpful to
1 thankful Users |
11/28/2017 5:06 PM | |
Posts: 241 Rating:
|
bit 4 in your picture isnt in my screen shot!! that was the problem confused me |
11/28/2017 7:15 PM | |
Joined: 6/4/2008 Last visit: 8/5/2025 Posts: 1518 Rating:
|
Of course, you are both correct due to byte swapping |
This contribution was helpful to
2 thankful Users |
11/29/2017 11:17 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8171 Rating:
|
New question published by kia123 is split to a separate thread with the subject Need to control micromaster_440 by modbus RTU with delta HMI B_series. Best regards |