1/5/2020 10:53 PM | |
Posts: 1 Rating: (0) |
3RW446-6BC44 Massage Error Bypass part fault. How can I resolve this problem in softstarter? ------------------------------------------------------------------------------------------ |
Last edited by: Kakku at: 01/05/2020 22:59:47Last edited by: Jen_Moderator at: 01/07/2020 06:39:57New subject after splitting |
|
1/10/2020 12:51 PM | |
Joined: 4/15/2009 Last visit: 8/26/2024 Posts: 125 Rating: (11)
|
Hello, following a description of the failure message “Bypass part fault” =defective -> bypass contactor welded or not closed. If the bypass contactor is welded the failure can detected if the current continue flow or on the missing zero crossings of the voltage. If the bypass contactor not close ( e.g. wires not connected) the zero crossings of the voltage are further present and the current flow further via the thyristors, not via the open bypass contactor. if the error still exists contact the Siemens technical support. Support Request:www.siemens.de/support-request Best regards |