I will check with it. I am using PM1207 for the power supply for all modules and also for the flow meter. I will check the power supply cables |
7/1/2019 4:44 PM | |
Joined: 9/19/2011 Last visit: 5/23/2023 Posts: 135 Rating:
|
Hello Jay, I believe that you have the correct wiring, but I just wanted to be sure. It is important that the 24V power supply return (M) be connected correctly. Attached is the correct wiring for three 2-wire sensors. Larry Attachment2-wire 3-sensor connections.pdf (94 Downloads) |