6/17/2011 5:56 PM | |
Posts: 947 Rating:
|
Hi! Check: Sinc modules and sync cable connected right? |
6/24/2011 5:21 AM | |
Posts: 35 Rating:
|
hello gre_m ; i remember the IFM1F is red in that time.after that we rastart the system ,then it's go into reduandant mode. how can you know the problem is syn-mode,and why no record in diag-buff. |
6/24/2011 8:25 AM | |
Posts: 947 Rating:
|
Hi jun-jun In your system the following problem: Both the CPU wants to become Master. It is impossible, and therefore redundant CPU goes into Stop. I have seen a situation where the wrong was connected cables sync: Lower socket CPU0 to the top socket CPU1, and the upper socket CPU0 to the lower socket CPU1. see: Event 54 of 120: Event ID 16# 43D4 A master has gone into STOP mode because its partner CPU is also a master (link-up error) STOP of: unknown (Z1: 0000) Validmaster is: unknown (Z2: 0000) Previous operating mode: STOP (internal) Requested operating mode: STOP (internal) Event occurred in the standby CPU in rack 1 Incoming event 05:19:27.308 PM 06/13/2011 What MLFB have your CPU? |
6/28/2011 10:18 AM | |
Posts: 35 Rating:
|
Hi gre_m: we used the cpu of 414-4hj04,vision is 4.0.10.now is work in runmode. thank gre_m. |