7/27/2014 6:55 PM | |
Joined: 3/31/2009 Last visit: 7/16/2024 Posts: 191 Rating: (3) |
Hii, i tried to connect s7400 using im463-2 to im314 s5 135u i/o. attached was my configuration. after i download the configuration to the s7400 plc, i get i/o access error on plc and the extf dan sf led was turn red.. please help, is there any wrong with my configuration. br rusli AttachmentIM463_2.pdf (163 Downloads) |
7/28/2014 3:44 AM | |
Joined: 3/31/2009 Last visit: 7/16/2024 Posts: 191 Rating: (3) |
Hii, Forget to mention that C2 led was green, and the module was ok. BR Rusli |
7/28/2014 9:32 AM | |
Joined: 10/7/2005 Last visit: 9/9/2024 Posts: 3019 Rating: (1054)
|
Hello rusli_rusli configuration, IM314 jumper settingsand the likes all look fine by me. Could be a hardware problem of course (faulty IM etc.), but first thing I'd suggest to checkare the LED's on the S5 power supplies in eachEU183 (perhaps 24V monitoring is enabled in the PS butnot externally supplied with24V and stuff like that). |
Cheers |
|