5/17/2013 12:36 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, Your adressing is o.k. for the onboard i/o I 136.0 to I 138.7, Q136.0 toQ 137.7. Did you connect the i/o as shown in attached pdf (don't forget the 24V) Regards, Marcjan Attachments7300_cpu_31xc_connection.pdf (34 Downloads) |
Problem solved? |
|
5/17/2013 1:01 PM | |
Posts: 13 Rating:
|
Hi, I dont have anything connected. Thats why i just use a normally closed switch and than I just want to set a LED as shown in the picture. |
5/21/2013 1:59 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, That's not new, DO always needed to be separatly powered. You can reed more about it in the Module data manual In the PDF i attached before you can see the connections at the terminals. There is no need to use 20 wires, simply wire from 1 module to the other. For testing your output you only have to wire 1 group of outputs. Regards, Marcjan |