5/18/2012 5:55 PM | |
Posts: 2964 Rating: (481)
|
Hello... 840D connected with PCU20/PCU50 ? MMC103 /MMC102 This look like data loss has happend in your case..you need to load clear NC and PLC and load your archive backups. check this link for clearing NC & PLC: /tf/WW/en/Posts/60254#top /tf/WW/en/Posts/45967#top 1) Does this look like what has happened? ==> Data LOSS you need to clear and restore your archive backups. Regards, Prakash |
5/18/2012 7:03 PM | |
Posts: 38 Rating: (0) |
Hi. Thanks for your help. If you wouldn't mind taking a look at the link below and letting me know if this is the battery in the 840D I should replace I would appreciate it. http://www.pqbattery.com/battery_specs.cfm/PLC-Batteries/SIEMENS/Sinumerik-840D-NCU-Battery/S74940-CR1/2AA-WSC-75013-1705 If this isn't the one where should I be looking. Thanks Nick Steele |
5/19/2012 2:09 PM | |
Posts: 38 Rating: (0) |
Thanks |
11/29/2013 8:43 AM | |
Joined: 4/24/2009 Last visit: 2/19/2024 Posts: 2683 Rating: (135) |
New question splitted to when the sinumerik boots up the keys on the controller unit panel starts flashing Best regards O_Moderator |