2/26/2020 5:14 PM | |
Joined: 9/3/2013 Last visit: 11/3/2023 Posts: 152 Rating: (31) |
Hello Mo.Sa See: https://support.industry.siemens.com/cs/de/en/view/109739941 chapter 6.2.3 Interlocks and chapter Feedbacks 1.1.3.4 ff Regards |
Last edited by: Technodrome at: 02/28/2020 09:25:32 |
|
This contribution was helpful to1 thankful Users |
2/27/2020 7:43 AM | |
Joined: 3/14/2008 Last visit: 9/13/2024 Posts: 2095 Rating: (936)
|
Hi Mo.Sa, It sounds like you are using the "Protect" command. Definition of protect is that you need to reset the command in order to start the motor again. However, when you use the "Intlock" command, you don't need to reset the motor first. After the Intlock is healthy again ("1" signal), the motor will start automatically when the automatic command is still "1". PS: For your info: With the "Permit" command, you make sure the motor cannot be started if Permit=0. This is only valid when the motor is not yet running. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
2/27/2020 8:55 PM | |
Joined: 2/29/2016 Last visit: 3/12/2024 Posts: 100 Rating: (1) |
Thx! I struggled with this to! |