10/24/2018 7:40 AM | |
Joined: 4/28/2015 Last visit: 9/9/2024 Posts: 3345 Rating: (379)
|
Hi, I assume that you have a flow which is not configured correctly. You can check it for example by starting node red manually with the command
and check the console output. If node-red crashes immediatly after startup it's becuase of the flow. You have to delete it on the device (see here). Before deleting I would suggest to copy the content of the file flows_iot2000.json and import it to node-red - without deploying it. So all your work won't be lost and you can check where the misconfigured node is. Best regards! |
Not working for IOT2050 support anymore from March 1st, 2024. |
|
10/24/2018 12:30 PM | |
Joined: 2/6/2015 Last visit: 11/8/2018 Posts: 2 Rating: (0) |
Hello, Have you tried deleting the flow? Kind regards! |
10/26/2018 8:04 AM | |
Posts: 10 Rating: (0) |
Hi. That was my guess, too. I can provide the flow file to you, just rename it. Attachmentflows_iot2000.txt (220 Downloads) |
10/26/2018 9:01 AM | |
Joined: 4/28/2015 Last visit: 9/9/2024 Posts: 3345 Rating: (379)
|
Hi, I have problems installing the s7comm node. I can install it via manage palette, but then I cannot deploy the flow and after reboot the node are gone. Are you using a S7-1500? Try to remove the last variable of your S7 connection. There is DB0 and no offset given. That does not exist in the PLC. Maybe that's the error. And I have to say that I have no experience with the s7comm node.. I always use the s7 node. Maybe removing the non-existing variable is the reason, let's see Best regards! |
Not working for IOT2050 support anymore from March 1st, 2024. |
|